Home > Forum > Operator terminals (Weintek) > How to find out the IP address of the iP and iE series terminals
- This topic has 1 replies, 2 participants and was last updated 5 years ago da Sergio Bertana.
-
AuthorPost
-
April 15, 2019 at 8: 42 am #47288GesuinoParticipant
I have an emergency with a Weintek panel model MT8051iP, in practice it works correctly but when I downloaded the project I left the panel with the IP address automatically (DHCP), then I was no longer able to perform other downloads, the system gives me the error of not communicating with the panel or incorrect IP.
In my project I don't leave the menu bar enabled and so I can't access the settings to change the IP address to the panel, when I restart the panel on the initial screen displays (os: 20171069 ip: DHCP).
How can I reset the panel and set it to the initial settings? How can I communicate with the panel in this situation?
April 15, 2019 at 8: 49 am #47290Sergio BertanaAdministrator ForumThe simplest solution is to connect the panel to a network in which there is a DHCP server, in this way the server assigns an IP to the panel, then a network scanning program is run (Example Advanced IP Scanner) and identify the IP assigned to the panel, in this way you can download a project that activates the system bar in the panel.
Another possibility is to load a project on the panel that activates the system tray via USB key.
Then with the active system bar you can access the network settings.
In terminals that have the "Touch Screen Calibration Mode" dip-switch, it is possible to close the switch to activate screen calibration (Forum), once the calibration has been completed it will be possible to return the terminal to the factory settings which require the display of the system bar.
-