I'm struggling with the MT8051iP terminal, it's been a while that I walk around without hitting the center….
I would need to make two 0/1 lamps disappear or display on the "Status" page, flashing in status 1, only if they have been enabled in the "configuration" page, the enabling and alarms are data exchanged and functioning with the SlimLine.
I tried with the multistate lamp with the “0” frame empty, but then it won't blink if it's in error. I couldn't find a magician's solution .. Please help me !!
Thanks for any answers ...
I don't know if I understood your request but to make an object visible / invisible, for example a lamp, just set the visibility of the object conditioned to a register in the security tab. See in this screenshot the settings that may be suitable for your purpose.
As variables I used bits inside the panel, instead you will have to use BOOL variables read by your PLC, which if you write is one SlimLine you will use 0x 40xxx variables.
Great, exactly what I was looking for ...