Home > Forum > Operator terminals (Weintek) > Problem viewing recipes with EasyAccess
- This topic has 3 replies, 1 participant and was last updated 2 years, 10 months ago da Sergio Bertana.
-
AuthorPost
-
June 3, 2021 at 12: 10 pm #60091StefanoParticipant
I use an MPS054B110 Cpu module and an MT8073IE panel, the connection with EasyAccess is Ok, from the remote PC I view and control everything I would do directly in front of the HMI but….
On the page of the panel dedicated to the management of recipes I have a "View recipe" object where I view the list of stored recipes and from which I select the desired recipe. From the PC connected via EasyAccess, the "View recipe" object is not populated, as opposed to the "Numeric" and "Ascii" fields which are regularly populated with the correct values.
Having not populated the view of the available recipes, I cannot remotely select the desired recipe. Am I getting lost in a glass of water or is this not possible?
June 3, 2021 at 12: 22 pm #60116Sergio BertanaAdministrator ForumTell me about the remote virtual display of the EasyAccess comn panel but you don't tell me what kind of display you use, On-Line simulation or a VNC client.
If you are using the On-Line simulation you are actually running a virtual panel running on a PC and in this case the recipe database is the one on your PC disk and not the one in the panel. In this case, this is why you are not seeing the recipes ...
A completely different speech is the use of a VNC client, in this case you operate exactly on the screen of the real panel all the maneuvers made are performed in parallel they see both the people who are in front of the panel and in front of the PC. In this case you don't have to have any problems.
June 3, 2021 at 2: 36 pm #60119StefanoParticipantI use EasyAccess directly, from the main page, on the only panel that I have registered for now, I click on the blue icon representing the panel.
But from your answer something is wrong, I can move between the pages, read the status of the variables and change them but the real operator panel does not move in parallel to what I see on the PC. it is not that they are also in On-Line simulation in this case.
June 3, 2021 at 2: 36 pm #60120StefanoParticipantI apologize is just as I assumed. The blue icon depicting the panel sends me only in online simulation.
By installing VNC everything works Ok
-