Home > Forum > Operator terminals (Weintek) > Return the “i” series terminals to default conditions
- This topic has 1 replies, 2 participants and was last updated 12 years, 4 months ago da Sergio Bertana.
-
AuthorPost
-
December 15, 2011 at 11: 20 am #35141AuthorlessIdle
I am with an MT8050i terminal in which a program has been loaded, the program disables the display of the system bar so I cannot access the IP address setting menu. Not knowing the IP assigned to the terminal, how can I do to restore the terminal to its default settings?
December 15, 2011 at 11: 26 am #37070Sergio BertanaAdministrator ForumThe maneuver to restore the "i" series terminals to their default conditions is indicated in the EasyBuilder 8000 manual, of which I am attaching extract.
In practice, the 1 switch must be brought into position with the terminal switched off On, this forces the screen calibration procedure, once the calibration is finished, the window that restores the system password to the default value is displayed "111111".
When this operation is completed, the terminal is switched off and all the switches are returned to their position off, then the terminal is turned on again. At this point, the button that allows access to the system settings will be visible at the bottom right of the display.
By touching the bar you access the system settings, the password "111111" is requested and it will be possible to set from the TAB Network the IP address of the terminal.
Warning! With reset all passwords are reset, so to be able to carry out the programming operations of the terminal it is necessary to activate the system settings and access the TAB Security and set up all the passwords with the desired values (Screenshot).
-